ClipperCreek HCS series
Revision as of 02:30, 26 July 2024 by ChrisC (talk | contribs) (formatting)
(up to EV chargers section)
LED fault codes table for HCS series
More advanced LED codes table from CC's "HCS Troubleshooting Guide". Note that the number of blinks of the two bottom red LEDs is important. If two blinks, then the line 1 side of the contactor is failing; if three blinks, then line 2.
Relay / contactor information
Two of the failure modes involve the contactor. This part is a Hongfa XMC0-402.IBBD , which is a 40-Amp, 2-pole contactor; see Hongfa's website for more on the XMC0 series. The Hongfa contactors catalog (PDF) includes XMC0 part number details on page 5/22, and cross references to other companies on page 2/22 (e.g. Tyco, Siemens). Other HCS-series units may have different make and model of contactors in them, but they should be drop-in replacements / compatible (and should be documented here if you encounter one).
Background / failure modes
  • High ground leakage
More product photos
inside view of HCS series EVSe, with back cover removed
lone PCBA inside the HCS series EVSE